24R Knowledge Base
Limit switches are the referees of your machine travel. They set your boundaries and stop you from going out of bounds. Listed below are some helpful troubleshooting tips, in the event you are having limit switch issues.
Limit light is always on, even though the switch is not actuated
Input Status Reported from the Status Tab
Test to Perform on the Wiring at the ECM Board
The X Limit light is always on, even though the switch is not actuated.
Jumper wire 455 to 485 on the ECM Board.
The Y Limit light is always on, even though the switch is not actuated.
Jumper wire 457 to 485 on the ECM Board.
The Z Limit light is always on, even though the switch is not actuated.
Jumper wire 459 to 485 on the ECM Board.
Results and conclusions:
  • If the light doesn’t go out when the terminals are jumped, the ECM board is defective.
  • If the light goes out when the terminals are jumped, the wiring has a break or the limit switch is defective.
Limit light is never on, even though the switch is actuated
The X Limit light is never on, even though the switch is actuated.
Remove wire 455 on the ECM Board.
The Y Limit light is never on, even though the switch is actuated.
Remove wire 457 on the ECM Board.
The Z Limit light is never on, even though the switch is actuated.
Remove wire 459 on the ECM Board.
  • If the light doesn’t go on when the wire is removed, the ECM Board is defective.
  • If the light goes on when wire is removed, the wiring has a short or the limit switch is defective:
    1. Power off the machine. Then, disconnect wires from the switch and tape the end of each wire to prevent shorts.
    2. Power on the machine.
    3. If the diagnostic light is on, the wiring is OK and the switch is defective.
    4. If the diagnostic light is off, the wiring has a short circuit.
If you continue to have issues, contact Tormach Technical Support.