1500MX Knowledge Base

Machine Won't Power On - 1500MX

Background

The idea of providing power to your machine seems simple: just plug it in. In reality, there are a number of other components used in order to provide power appropriately safety for you and the machine, including (but not limited to):

  • The main disconnect switch

  • Fuses and/or circuit breakers

  • Emergency stop switch/button

  • Separate latching circuits for the spindle and rest of the machine

  • Transformers, which change the electricity to the appropriate value

Even with all of these components, you can systematically locate nearly any problem with just a multimeter.

Tools

  • Digital multimeter

Reseat the NEMA L6-30 Plug Into an Outlet

Reason: The machine plug isn’t plugged in to an outlet.

  1. Verify that the main power plug is plugged into a known working outlet.

  2. If needed, measure for 208-240 Vac between wires 1001 and 1002/N at the DISC1 Main Disconnect.

image-20250930-163448.png
Wires 1001 - 1002/N
image-20250930-163344.png
Main Disconnect (DISC1) Location

Reset Facility’s Breaker for Machine Circuit

Reason: The facility’s mains breaker is tripped.

  1. Examine power cable for damage or exposed wires, and then reset your facility’s circuit breaker serving the machine.

  2. If needed, measure for 208-240 Vac between wires 1001 and 1002/N at the DISC1 Main Disconnect. (See images above)

Reset the CB1 Circuit Breaker In the Machine

Reason: The CB1 breaker is tripped.

  1. If the mill, controller, accessories, and enclosure lights don’t have power, examine the power cords and wires for damaged or exposed wires, and then reset the CB1 circuit breaker.

  2. If needed, measure for 208-240 Vac between wires 1005 and 1006/N at the CB1 circuit breaker.

image-20250930-171042.png
Wires 1005 - 1006/N
image-20250930-171058.png
CB1 Location

Check the Position of the Main Disconnect Switch

Reason: The Main Disconnect switch is in the OFF position.

  1. Switch DISC1 Main Disconnect to the ON position.

  2. If needed, measure for 208-240 Vac between wires 1003 and 1004/N at the DISC1 Main Disconnect.

image-20250930-171802.png
Wires 1003 - 1004/N


image-20250930-163344.png
Main Disconnect (DISC1) Location

Verify the Machine is Out of Emergency Stop Condition

Reason: The Emergency Stop is pushed in.

  1. Twist out the Emergency Stop button and press the Reset button.

Check the DC Power Supply

Reason: The DC power supply is defective.

  1. Check if Electrical Cabinet Fan (FAN1) and Spindle Motor Fan (FAN2) are running.

  2. Check for DC OK LED on the PS1 DC power supply.

  3. Check for Control Power (D37) LED on E1 Servo IO Breakout Board.

  4. Measure for 208 Vac-240 Vac between wires 1032 and 1033/N at the PS1
    DC power supply.

  5. Measure for 24 Vdc nominal between wires 4001 and 4002 at the PS1 DC
    power supply.

image-20251001-145429.png
Wire 1032 - 1033/N and 4001 - 4002 Location


image-20251001-142508.png
Electrical Cabinet Fan (FAN1)


image-20251001-142637.png
Spindle Motor Fan (FAN2) Location


image-20251001-144000.png
DC Power Supply (PS1) Location
image-20251001-144831.png
Servo IO Breakout Board (E1) Location


Adjust the DC Power Supply PS1 Output Voltage

Reason: The DC power supply PS1 output voltage is too low.

  1. Check if Electrical Cabinet Fan (FAN1) and Spindle Motor Fan (FAN2) are running. (See images above)

  2. Check for DC OK LED on PS1 DC power supply. (See images above)

  3. Measure for 208-240 Vac between wires 1032 and 1033/N at the PS1 DC power supply. (See images above)

  4. Measure for 24 Vdc nominal between wires 4001 and 4002 at the PS1 DC power supply. (See images above)

  5. If output voltage is less than 24 Vdc, adjust the output voltage using the +V ADJ trim potentiometer on the front of the PS1 DC power supply.

Reset Machine Circuit Breakers

Reason: The CB1, CB2, or CB4 circuit breaker tripped.

  1. Examine the power cords and wires for damaged or exposed wires, and then reset the circuit breaker.

  2. If needed, measure for 208-240 Vac between wires 1005 and 1006/N at the CB1 circuit breaker, between wires 1013 and 1014/N at the CB2 circuit breaker, and between wires 1020 and 1021/N at the CB4 circuit breaker.

image-20251001-184154.png
Breaker Output Wire Locations


image-20251001-183949.png
Circuit Breaker Locations